CK: Yes your right, but I try to do all my work that way. (a Step Up)
Forgive this old wire twister for a moment while I run the numbers for the benefit of those who don't know why I (we) do work a certain way.
1000 watt output (KW) amp X 1.50 (efficiency quotient) = approx 1500 Total power watts
Nominal house circuit of 15 amps @ 120 volt = 1800 watts total power
Yep sounds adequate, correct ?
Then one must consider the little NEC clause that states in today's code, that no
branch circuit shall be used in
continuous service at more than 75% of the rated breaker size.
Hmmm....So a 15 amp circuit should now not be loaded more than 11.25 amps (call it 12 amps)...
Recalculating
120v @ 12 amps = 1440 watts....But! But my amp needs 1500 watts to work at full output....BINGO BABY! Houston we have a problem
OK OK! Yes a KW (ssb/cw) amp is
not considered a continuous service device.
Then Ladies and Gents are we running our 100 watt rig on the same circuit?
Let's not forget the 75 watt desk lamp and the small fan to keep the shack comfortable.
Yes Houston we are experiencing some issue....It's called voltage drop....
OK OK! Enough Soapbox material from the OLD wire twister...
The point in all of this is...If your budget is forgiving enough for you to have all this nice gear, don't cheat on the service that your using to operate it with.
This goes for any device in your home/office etc....give yourself a little headroom...don't push the edge...
Sometimes an edge can cut you in ways you may not like!
All the Best
Gary